Welcome to the DIY Audio Projects Message Forum. Use these forums to discuss Hi-Fi audio and to share your DIY Audio Projects. Registration is free and required to post messages and view the file attachments. Registration will only take a minute and registered users do not see any advertisements. After you have completed the online registration process, check your email (including spam/junk folder) for the verification email to activate your account. New members are under moderation - so your posts will not be visible until approved by a moderator. See the Read Me 1st, Forum RULES and Forum FAQ to get started on the forum.

It is currently 16 Aug 2018, 20:48

All times are UTC - 6 hours [ DST ]




Post new topic Reply to topic  [ 12 posts ]  Go to page 1, 2  Next
Author Message
 Post subject: Fuses
PostPosted: 28 Jan 2018, 10:39 
Offline
User avatar

Joined: 01 Jun 2013, 09:05
Posts: 655
I thought it might be interesting to look at fuses,

Most people already know this but for any others.

Fault clearance time is the time from fault current to when fault current stops.
At the moment of a fault the fuse is just a wire so the supply will deliver the maximum current that can be drawn from it.
At this point the fuse element will begin to heat based upon volt drop and current drawn.
When the element breakes, the gases and arc continue to deliver fault current until the gap/arc can no longer sustain conduction.
NB this clearence is different between AC and DC supplies, where the AC voltage changes and reduces arc distance.
On DC the votage remains constant so the arc is sustained and more difficult to break, also any capacitors or storage can deliver high current pulses
where the energy dissipated in the fault is based upon discharge times and current/voltage. Where the voltage can sustain the arc.
On high energy disruption it is possible for a cartridge fuse to rupture or explode due to expanding gasses and heating effect.
Some designs use fuse elements under tension which pull apart as the fuse operates, others are filled with silica/sand which falls into the gap in the element during operation to help quench the arc.

On a cartridge fuse, fusing current is 1.5 times the rated value.
Some fuses are rated for slow blow where a large inrush or magnetisation current happens at switch on eg toroid Tx.
This would blow a fuse at power on.
Quick blow is used where fast action is required for electronics where a surge would cause significant damage but no inrush surge takes place.
Fuses have a voltage rating!

Regards
M. Gregg

_________________
What is the sound of one hand clapping?


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 28 Jan 2018, 17:13 
Offline
Project Author
User avatar

Joined: 04 Jun 2008, 20:59
Posts: 3748
Location: Arizona, USA
Hi, Yes a good idea to keep in mind. If you use a 100 amp one and it will never blow. :eek: :eek: For tube gear I recommend a slow blow rated at about 2 times the expected current. For normal fuses I use 3-4 times the expected current. Any less and you will be replacing fuses often when there is no failure. My experience is that any significant failure in tube gear especially power amps will easily blow a fuse many times the ratings I indicated. Fortunately tube gear itself is rather hardy and need not have instaneous fuse action. Some SS gear however is not so tolerant.

Good listening
Bruce

_________________
Some of my DIY Tube Amplifier Projects:


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 28 Jan 2018, 17:38 
Offline
User avatar

Joined: 08 Aug 2009, 03:11
Posts: 2225
Location: Chilliwack, BC
Fusing lso depends on the transformer, too.

Example, a 25VA EI core can use a 250mA fast-blow and be OK during normal operation. A 25VA toroid will vapourize it in a nanosecond, so I use slow-blow for them due to magnetizing current surge.

I also use slow-blow if things with heaters are involved, to take the surge.

Cheers!

_________________
-= Gregg =-
* Ratings are for transistors - tubes have guidelines*
Home: GeeK ZonE
Work: Classic Valve Design


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 28 Jan 2018, 19:22 
Offline
Project Author
User avatar

Joined: 06 Apr 2009, 10:08
Posts: 1446
Location: US Pacific Northwest
Some very good information of fuses and fusing here:

http://www.littelfuse.com/~/media/electronics/product_catalogs/littelfuse_fuseology_selection_guide.pdf.pdf

_________________
Matt
It's all about the Glass!
http://www.CascadeTubes.com
Cascade Tubes Blog


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 28 Jan 2018, 20:23 
Offline
User avatar

Joined: 08 Aug 2009, 03:11
Posts: 2225
Location: Chilliwack, BC
They need to do a "Readers Digest" version for those of us with low attention sp... SQUIRREL! :D

_________________
-= Gregg =-
* Ratings are for transistors - tubes have guidelines*
Home: GeeK ZonE
Work: Classic Valve Design


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 29 Jan 2018, 04:25 
Offline
User avatar

Joined: 01 Jun 2013, 09:05
Posts: 655
I use inrush suppressors,

On most projects, but I think they are a "must fit" with toroid transformers.
It also means you can fuse closer to the running current so you don't have to fit massively over rated fuses.
I do use polyswitch solid state fuses on heater circuits.

Some people use microwave fuses for high voltage clearence.

I use capacitor quench across none safety critical fuses it stops them exploding on HV.
The sound of a fuse<<lets not go there. :D

I think its interesting for newbies to realise the energy that goes into a fault at the instant it happens before a fuse blows
and that the clearance time limits the energy into the fault and heating effect.
But remember the fuse is just a "piece of wire" so it has no magical properties at the moment of short circuit.

Regards
M. Gregg

_________________
What is the sound of one hand clapping?


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 29 Jan 2018, 04:33 
Offline
User avatar

Joined: 01 Jun 2013, 09:05
Posts: 655
Geek wrote:
They need to do a "Readers Digest" version for those of us with low attention sp... SQUIRREL! :D


Yes I know fuses are dead boring :D
So I thought a quick thread would cut through the fact that many people just fit them but don't actually know how they work or how to rate them.
Things like voltage rating gets lost with many thinking there is only a current rating.
Also the effect of DC Vs AC on fusing and clearance times.

Regards
M. Gregg

_________________
What is the sound of one hand clapping?


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 29 Jan 2018, 15:58 
Offline
User avatar

Joined: 08 Aug 2009, 03:11
Posts: 2225
Location: Chilliwack, BC
M. Gregg wrote:
Things like voltage rating gets lost with many thinking there is only a current rating.
Also the effect of DC Vs AC on fusing and clearance times.


Too true!

Arc quenching should also be a consideration with large transformers - those sand filled or "ceramic microwave oven" fuses as they're commonly known.

I had a Citation PA in that blew fuses and a regular one went *ssssst* as it blew, with a bright light that shone out of the holder. Orig. spec was the spring-loaded ones, but I had sand-filled ones on hand. Blew one more before tracking the issue, but no *ssssst*, just opened normally :up:

Cheers!

_________________
-= Gregg =-
* Ratings are for transistors - tubes have guidelines*
Home: GeeK ZonE
Work: Classic Valve Design


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 30 Jan 2018, 18:01 
Offline

Joined: 23 Feb 2017, 02:02
Posts: 132
I used a 0.5amp fuse for 220v. It didn't save my transformer from buring up after washed with water.
I went for a shower came back and one of the 230v coils gone bad.

I tested the fuse and blows at arround 0.6amps
Power draw is arround 18wats during idle


Top
 Profile  
 
 Post subject: Re: Fuses
PostPosted: 02 Feb 2018, 10:08 
Offline
User avatar

Joined: 01 Jun 2013, 09:05
Posts: 655
KochiyaYamato wrote:
I used a 0.5amp fuse for 220v. It didn't save my transformer from buring up after washed with water.
I went for a shower came back and one of the 230v coils gone bad.

I tested the fuse and blows at arround 0.6amps
Power draw is arround 18wats during idle


Thats because the fuse is meant to clear the fault after fuse ruptures.
Ie when the fault happens maximum current into fault is max supply capability.
https://en.wikipedia.org/wiki/Prospecti ... it_current

So no the fuse won't stop the fault happening.
Its not meant to protect the equipment just prevent a fire and damage to wires and cables.
If a component fails or insulation break down then that's it component is no longer serviceable.
The fuse is just damage limitation.
Its not a current limiter.

Regards
M. Gregg

_________________
What is the sound of one hand clapping?


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 12 posts ]  Go to page 1, 2  Next

All times are UTC - 6 hours [ DST ]


Who is online

Users browsing this forum: No registered users and 4 guests


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Jump to:  
DIY Tube Projects :: DIY Tube Amp Kits :: DIY Speaker Projects :: DIY Solid State Projects :: DIY IC / Op-amp Projects :: DIY Phono Projects :: DIY Cable Projects :: Hi-Fi Audio Schematics
© diyAudioProjects.com - Terms of Service - Privacy Policy